Re: onan help
I have not run across one that ever did that.
I will look into it for you tomorrow.
I am an Onan repair tech and have worked on many of those....
A 7500 diesel should be a variable speed inverter/generator......Yes?
Unfortunately the inverter section is a sealed unit and the control is part of that inverter section....NOT serviceable....
I will look at a machine's electrical print and trace out the starter circuitry but it is not a good scenario since you have changed most components already.....
If you can give me the Model Info off the I.D. label it would help.....
Looking in the Service Manual for a typical Cummins-Onan 7500 diesel inverter-generator this morning did not show me anything that is likely to be a simple fix for this machine.
The starter is controlled directly by the Controller PC board located inside the Inverter section and as I said not serviceable...
The starter should be de-energized when the engine reaches 800 rpm and the controller is always monitoring engine speed from output of the generator end......
Unless a wire is damaged, shorted, or possibly output is incorrect.......your Inverter-Controller is likely bad.
Not an uncommon issue on those units and since it is 20 years old.....anything is possible......
I would start the unit with the covers removed and pull the starter solenoid B+ wire off the starter and put a voltmeter on it to see if it is actually re-energizing after the unit is running.
I would also monitor output power and see if there is anything changing there at the same time.
The Inverter-generators can do some very difficult to diagnose things...
I had one that would "full field" the power end during cranking. The starter could barely turn the engine over due to the high field strength.....You think the starter or battery/cables are bad but it was the Inverter-control unit....